Apprentice answerWhat is the required clearance to combustibles for a Type 1 grease duct (black iron)
3rd YearGrease Duct & Specialty ExhaustStop / Verify
Per the International Mechanical Code (IMC Section 506), a standard, uninsulated Type 1 commercial kitchen grease duct must maintain a strict minimum of 18 inches of clearance to any combustible materials (like wood framing or drywall).
Ask a jobsite questionBack to Grease Duct & Specialty Exhaust
Plain-English answer
Per the International Mechanical Code (IMC Section 506), a standard, uninsulated Type 1 commercial kitchen grease duct must maintain a strict minimum of 18 inches of clearance to any combustible materials (like wood framing or drywall).
The Fix: This clearance can only be reduced if you wrap the duct in an ICC-ES listed field-applied multi-layer fire barrier blanket system (like 3M Fire Barrier or FireMaster wrap).
Field checklist
- Stop and verify the approved detail, manufacturer instructions, foreman direction, and project specs before touching it.
- Per the International Mechanical Code (IMC Section 506), a standard, uninsulated Type 1 commercial kitchen grease duct must maintain a strict minimum of 18 inches of clearance to any...
Ask Foreman
Hey boss, I’m on specialty duct and need verification before I touch this: What is the required clearance to combustibles for a Type 1 grease duct (black iron)? Do you want me to stop here and check the approved detail, submittal, or inspector/manufacturer requirement first?
Verify before acting
Use this as training guidance. The foreman, approved drawings, project specs, manufacturer installation instructions, employer safety policy, and AHJ/code requirements always control the final answer.