What's the trick to installing fire-wrap (Zero Clearance insulation) on grease duct

3rd YearInsulation, Liner & CondensationStop / Verify

Foil-faced fire wrap must be installed in a two-layer system with staggered joints.

Ask a jobsite questionBack to Insulation, Liner & Condensation

Plain-English answer

Foil-faced fire wrap must be installed in a two-layer system with staggered joints.

Cut the blanket wrap so it tightly hugs the duct profiles, and create a minimum 3-inch perimeter overlap at all sheet edges. Secure the heavy wrap tightly to the metal using stainless steel banding straps spaced every 10 to 12 inches, or use heavy-duty stainless steel weld pins.

Field checklist

Ask Foreman

Hey boss, I’m on specialty duct and need verification before I touch this: What's the trick to installing fire-wrap (Zero Clearance insulation) on grease duct? Do you want me to stop here and check the approved detail, submittal, or inspector/manufacturer requirement first?

Verify before acting

Use this as training guidance. The foreman, approved drawings, project specs, manufacturer installation instructions, employer safety policy, and AHJ/code requirements always control the final answer.