Apprentice answerWhat do I check when a branch reads zero CFM but dampers are open
3rd YearDampers, Fire/Smoke & Life SafetyCheck first
Zero CFM with open dampers usually means a real blockage, closed/tripped device, wrong connection, or disconnected path. Trace the branch before blaming the balancer.
Ask a jobsite questionBack to Dampers, Fire/Smoke & Life Safety
Plain-English answer
If the unit is running and dampers are open but a branch reads zero, something is stopping the air. It may be internal packing/shipping material, a closed fire/smoke damper, blocked VAV inlet, crushed flex, disconnected duct, wrong tap, or a damper blade not actually moving.
The field move is to trace the air path from main to outlet and inspect at each choke point. Use existing access, registers, camera/mirror, pressure/noise clues, and photos. Cut access only with approval and patch it correctly.