Can standard spiral duct be used for commercial kitchen grease exhaust?

3rd YearRED · Stop and get directionKitchen Exhaust / Grease

Short answer

No. Treat grease/liquid exhaust construction as a stop item. Standard spiral lockseam is not a field patch for grease service.

Field answer

Kitchen grease or liquid-bearing exhaust needs approved liquid-tight construction. Lockseam spiral can leak through the seam and create sanitation, fire, and inspection problems.

Stop the work, identify the system type, and verify the required listed/welded material, cleanouts, slope, wrap/clearance, and inspection detail before continuing.

What to check first

Do not do this

Do not use mastic to make standard spiral pipe into grease duct.

Why it matters

Wrong grease exhaust construction can create fire risk, health issues, failed inspection, and major rework.

Ask foreman

This kitchen/dishwasher exhaust at [location] appears to be standard spiral lockseam and is leaking liquid/grease. I stopped work. Do you want this held for the approved grease-exhaust material/detail?

Text this wording

Related Field Rescue route

Open routeBack to Q&A

Final direction belongs to the foreman, approved drawings/specs, manufacturer instructions, pressure/material schedule, employer policy, and AHJ/code requirements.