Apprentice Q&A · #300Should seismic restraint cables have slack in them?
3rd YearSeismic / Cable RestraintsYELLOW · Check First
Seismic cables should restrain movement without pulling the duct out of line. Remove sloppy slack and adjust them per the approved seismic detail.
Search Field RescueSearch Q&AOpen related route
Answer
A loose seismic cable lets the duct swing before the cable catches it. That momentum can shock-load anchors, rods, and other trades.
Check the approved seismic layout, cable direction, anchor points, and whether tightening the cable pulls the main hangers out of plumb. Adjust to the required condition and document for inspection.
Field checks
- Check lateral and longitudinal brace locations.
- Look for slack loops, wrong angles, or cable rubbing other trades.
- Tension only per approved seismic detail.
- Verify main rods remain plumb.
- Photo-document before inspection if needed.
Ask foreman
The seismic cables on [run/location] have visible slack. I checked the brace direction and rods. Do you want them tightened per detail before inspection?
Text this
Do not do this
Do not leave seismic cable loops hanging loose because they “look safer.”
Why this matters
Loose seismic restraints can fail inspection and let ductwork swing hard during movement.
Final direction still comes from approved drawings, specs, manufacturer instructions, employer policy, foreman/detailer direction, structural/seismic details, and AHJ/code requirements.